I have some problems with elements solid226 (for thermal + structural analysis) and reinf264 to make them work correctly together in a different temperatures then a normal one (room - approx.20°C).
It seems like the material model "MISO" defined in dependance on temperature for the elements REINF264 applied into base elements solid226 is not working the correct way. The tamperature of the reinforcement elements is shown correctly, something around the temperature of the base ones, but then it achieves stress which should not be achieved in that temperature.
If the elements solid185 are used as the base ones, the stress - strain dependance of the reinf elements seems to be reasonable there. (although so far I have not achieved succesfully some higher temperatures the structure should withstand, but at least it behaves not the same way as if there is normal room temperature)
any experience with using these elements together?
  • edited July 2018
    Hello Dadojin,
      When you say it doesn't work correctly, can you please elaborate and show some pictures? It would in general help if you could post snapshots about to model/settings?
    Sandeep
  • DadojinDadojin Member
    edited July 2018
    ! ------- GEOMETRIA -------
    xxxx=2.000! 1/2 rozpatia
    yyyy=0.075! 1/2 vysky
    zzzz=0.075! 1/2 sirky
    rozmerelementu=0.025
    /PREP7
    K,1,0,0,0
    K,2,0,-1*yyyy,0
    K,3,0,yyyy,0
    K,7,0,-1*yyyy,zzzz
    K,8,0,0,zzzz
    K,9,0,yyyy,zzzz
    A,8,1,3,9
    A,7,2,1,8
    KSEL,S,LOC,X,0
    LSLK,S,1
    ASLL,S,1
    VEXT,ALL,,,xxxx-yyyy,
    KSEL,S,LOC,X,xxxx-yyyy
    LSLK,S,1
    ASLL,S,1
    VEXT,ALL,,,yyyy,
    KSEL,S,LOC,X,xxxx
    LSLK,S,1
    ASLL,S,1
    VEXT,ALL,,,yyyy
    ! velkosti
    ALLS
    KSEL,S,LOC,X,0
    LSLK,S,1
    LSLK,A,1
    KSEL,S,LOC,X,xxxx
    LSLK,A,1
    KSEL,S,LOC,X,xxxx+yyyy
    LSLK,A,1
    CM,ciary_z_y,lines
    LESIZE,ALL,rozmerelementu, , , ,1, , ,1,
    ALLS
    KSEL,S,LOC,X,0
    KSEL,A,LOC,X,xxxx-yyyy
    LSLK,S,1
    CMSEL,U,ciary_z_y
    CM,ciary_nosnik,lines
    LESIZE,ALL,2*rozmerelementu, , ,3,1, , ,1,
    ALLS
    KSEL,S,LOC,X,xxxx
    LSLK,S,0
    CMSEL,U,ciary_z_y
    CMSEL,U,ciary_nosnik
    CM,ciary_podpora,lines
    LESIZE,ALL,yyyy, , , ,1, , ,1,
    ALLS
    /REPLO
    ! ------- DEFINOVANIE BETONU -------
    ! - ELASTIC CONSTANTS - C25/30
    beton=25! OZNACENIE ELEMENTU <-----
    joungov_bet =31E9 ! [Pa]
    poisson_bet =0.2! [-]
    epsilon_c1 =0.0021! [-]
    epsilon_cu1 =0.0035! [-]
    hustota_bet =2300! [kg/m^3]
    ET,beton,SOLID226! element
    KEYOPT,beton,1,11! structural + thermal
    ! KEYOPT,beton,2,1 ! 0 = strong / 1 = weak coupling
    ! Joungov modul pruznosti a poissonov koeficient
    MPTEMP,,,,,,,,
    MPTEMP,1,0
    MPTEMP,2,20
    MPTEMP,3,57
    MPTEMP,4,100
    MPTEMP,5,200
    MPTEMP,6,300
    MPTEMP,7,400
    MPTEMP,8,500
    MPTEMP,9,600
    MPTEMP,10,700
    MPTEMP,11,800
    MPTEMP,12,900
    MPTEMP,13,1000
    MPTEMP,14,1100
    MPTEMP,15,1200
    MPDATA,EX,beton,,31E9
    MPDATA,EX,beton,,29.13421E9
    MPDATA,EX,beton,,24.79518E9
    MPDATA,EX,beton,,20.45614E9
    MPDATA,EX,beton,,16.11711E9
    MPDATA,EX,beton,,11.77807E9
    MPDATA,EX,beton,,3.9E9
    MPDATA,EX,beton,,3.1E9
    MPDATA,EX,beton,,2.48E9
    MPDATA,EX,beton,,1.86E9
    MPDATA,EX,beton,,1.24E9
    MPDATA,EX,beton,,0.62E9
    MPDATA,EX,beton,,1
    MPDATA,NUXY,beton,,poisson_beton
    ! dlzkova teplotna roztaznost
    ! Kremicite kamenivo
    MPTEMP,,,,,,,,
    MPTEMP,1,0
    MPTEMP,2,20
    MPTEMP,3,100
    MPTEMP,4,200
    MPTEMP,5,300
    MPTEMP,6,400
    MPTEMP,7,500
    MPTEMP,8,600
    MPTEMP,9,700
    MPTEMP,10,1200
    MPDATA,THSX,beton,,0
    MPDATA,THSX,beton,,0.000000184
    MPDATA,THSX,beton,,0.000743
    MPDATA,THSX,beton,,0.001804
    MPDATA,THSX,beton,,0.003141
    MPDATA,THSX,beton,,0.004892
    MPDATA,THSX,beton,,0.007195
    MPDATA,THSX,beton,,0.010188
    MPDATA,THSX,beton,,0.014
    MPDATA,THSX,beton,,0.0141
    !  Menetrey-Willam beton, exponencialne zmakcenie, kamenivo kremicite
    Rc =33E6! [Pa] - uniaxial compressive strength
    Rt =2.6E6! [Pa] - uniaxial tensile strength
    psi =11.5! [°] - dilatancy angle
    TB,CONCRETE,beton,15,,MW
    TBTEMP,0
    TBDATA,1,33E6,2.6E6,39.6E6
    TBTEMP,20
    TBTEMP,57
    TBTEMP,100
    TBTEMP,200
    TBDATA,1,31.35E6,2.08E6,37.62E6
    TBTEMP,300
    TBDATA,1,28.05E6,1.56E6,33.66E6
    TBTEMP,400
    TBDATA,1,24.75E6,1.04E6,29.7E6
    TBTEMP,500
    TBDATA,1,19.8E6,0.52E6,23.76E6
    TBTEMP,600
    TBDATA,1,14.85E6,3.5  ,17.82E6
    TBTEMP,700
    TBDATA,1,9.9E6,3  ,11.88E6
    TBTEMP,800
    TBDATA,1,4.95E6,2.5  ,5.94E6
    TBTEMP,900
    TBDATA,1,2.64E6,2  ,3.168E6
    TBTEMP,1000
    TBDATA,1,1.32E6,1.5  ,1.584E6
    TBTEMP,1100
    TBDATA,1,0.33E6,1  ,0.396E6
    TBTEMP,1200
    TBDATA,1,1  ,0.5  ,1.2
    TB,CONCRETE,beton,2,,DILA
    TBTEMP,0
    TBDATA,1,psi
    TBTEMP,1200
    TBDATA,1,psi
    TB,CONCRETE,beton,15,,HSD2
    TBTEMP,0
    TBDATA,1,0.00143548,0.01935831,0.4,0.6028,0.2,65
    TBDATA,7,0.1
    TBTEMP,20
    TBDATA,7,0.1
    TBTEMP,57
    TBDATA,1,0.00212923,0.02051456,0.4,0.6028,0.2,65
    TBDATA,7,0.1
    TBTEMP,100
    TBDATA,1,0.00286731,0.02181722,0.4,0.6028,0.2,65
    TBDATA,7,0.1
    TBTEMP,200
    TBDATA,1,0.00423564,0.02423785,0.4,0.6028,0.2,65
    TBDATA,7,0.1
    TBTEMP,300
    TBDATA,1,0.00562877,0.02667343,0.4,0.6028,0.2,65
    TBDATA,7,0.1
    TBTEMP,400
    TBDATA,1,0.00846436,0.02907432,0.4,0.6028,0.2,65
    TBDATA,7,0.1
    TBTEMP,500
    TBDATA,1,0.01331891,0.03148664,0.4,0.6028,0.2,65
    TBDATA,7,0.1
    TBTEMP,600
    TBDATA,1,0.02119231,0.03270473,0.4,0.6028,0.2,65
    TBDATA,7,0.1
    TBTEMP,700
    TBDATA,1,0.02180645,0.03557493,0.4,0.6028,0.2,65
    TBDATA,7,0.1
    TBTEMP,800
    TBDATA,1,0.02300403,0.03879683,0.4,0.6028,0.2,65
    TBDATA,7,0.1
    TBTEMP,900
    TBDATA,1,0.02358065,0.04164442,0.4,0.6028,0.2,65
    TBDATA,7,0.1
    TBTEMP,1000
    TBDATA,1,0.02393548,0.04435831,0.4,0.6028,0.2,65
    TBDATA,7,0.1
    TBTEMP,1100
    TBDATA,1,0.02446774,0.04717916,0.4,0.6028,0.2,65
    TBDATA,7,0.1
    TBTEMP,1200
    TBDATA,1,0.025,0.048,0.4,0.6028,0.2,65
    TBDATA,7,0.1
    ! Definicia hustoty betonu [kg / m^3 ]
    MPTEMP,,,,,,,,
    MPTEMP,1,0
    MPTEMP,2,20
    MPTEMP,3,115
    MPTEMP,4,200
    MPTEMP,5,400
    MPTEMP,6,1200
    MPDATA,DENS,beton,,hustota_bet
    MPDATA,DENS,beton,,0.98*hustota_bet
    MPDATA,DENS,beton,,0.95*hustota_bet
    MPDATA,DENS,beton,,0.88*hustota_bet
    ! Definicia mernej tepelnej kapacity betonu c [J/ (kg*K) ]
    ! pre vlhkost 1,5% hmotnosti betonu
    MPTEMP,,,,,,,,
    MPTEMP,1,0
    MPTEMP,2,20
    MPTEMP,3,100
    MPTEMP,4,101
    MPTEMP,5,115
    MPTEMP,6,200
    MPTEMP,7,400
    MPTEMP,8,1200
    MPDATA,C,beton,,900
    MPDATA,C,beton,,900
    MPDATA,C,beton,,900
    MPDATA,C,beton,,1470
    MPDATA,C,beton,,1000
    MPDATA,C,beton,,1100
    ! Definicia tepelnej vodivosti lambda [W/ (m*K) ]
    ! Dolna medz
    MPTEMP,,,,,,,,
    MPTEMP,1,0
    MPTEMP,2,20
    MPTEMP,3,100
    MPTEMP,4,200
    MPTEMP,5,300
    MPTEMP,6,400
    MPTEMP,7,500
    MPTEMP,8,600
    MPTEMP,9,700
    MPTEMP,10,800
    MPTEMP,11,900
    MPTEMP,12,1000
    MPTEMP,13,1100
    MPTEMP,14,1200
    MPDATA,KXX,beton,,1.36
    MPDATA,KXX,beton,,1.333028
    MPDATA,KXX,beton,,1.2297
    MPDATA,KXX,beton,,1.1108
    MPDATA,KXX,beton,,1.0033
    MPDATA,KXX,beton,,0.9072
    MPDATA,KXX,beton,,0.8225
    MPDATA,KXX,beton,,0.7492
    MPDATA,KXX,beton,,0.6873
    MPDATA,KXX,beton,,0.6368
    MPDATA,KXX,beton,,0.5977
    MPDATA,KXX,beton,,0.57
    MPDATA,KXX,beton,,0.5537
    MPDATA,KXX,beton,,0.5488
    ! ------- DEFINOVANIE PODLOZKY -------
    podlozka = 500! OZNACENIE ELEMENTU <-----
    ET,podlozka,SOLID226! element
    KEYOPT,podlozka,1,11! structural + thermal
    ! KEYOPT,podlozka,2,1 ! 0 = strong / 1 = weak coupling
    MPTEMP,,,,,,,,
    MPTEMP,1,0
    MPTEMP,2,20
    MPTEMP,3,57
    MPTEMP,4,100
    MPTEMP,5,200
    MPTEMP,6,300
    MPTEMP,7,400
    MPTEMP,8,500
    MPTEMP,9,600
    MPTEMP,10,700
    MPTEMP,11,800
    MPTEMP,12,900
    MPTEMP,13,1000
    MPTEMP,14,1100
    MPTEMP,15,1200
    MPDATA,EX,podlozka,,31E9
    MPDATA,EX,podlozka,,29.13421E9
    MPDATA,EX,podlozka,,24.79518E9
    MPDATA,EX,podlozka,,20.45614E9
    MPDATA,EX,podlozka,,16.11711E9
    MPDATA,EX,podlozka,,3.9E9
    MPDATA,EX,podlozka,,3.1E9
    MPDATA,EX,podlozka,,2.48E9
    MPDATA,EX,podlozka,,1.86E9
    MPDATA,EX,podlozka,,1.24E9
    MPDATA,EX,podlozka,,0.62E9
    MPDATA,NUXY,podlozka,,poisson_beton
    MPTEMP,,,,,,,,
    MPTEMP,1,0
    MPTEMP,2,20
    MPTEMP,3,100
    MPTEMP,4,200
    MPTEMP,5,300
    MPTEMP,6,400
    MPTEMP,7,500
    MPTEMP,8,600
    MPTEMP,9,700
    MPTEMP,10,1200
    MPDATA,THSX,podlozka,,0
    MPDATA,THSX,podlozka,,0.000000184
    MPDATA,THSX,podlozka,,0.000743
    MPDATA,THSX,podlozka,,0.001804
    MPDATA,THSX,podlozka,,0.003141
    MPDATA,THSX,podlozka,,0.004892
    MPDATA,THSX,podlozka,,0.007195
    MPDATA,THSX,podlozka,,0.010188
    MPDATA,THSX,podlozka,,0.014
    MPDATA,THSX,podlozka,,0.0154
    MPTEMP,,,,,,,,
    MPTEMP,1,0
    MPTEMP,2,20
    MPTEMP,3,115
    MPTEMP,4,200
    MPTEMP,5,400
    MPTEMP,6,1200
    MPDATA,DENS,podlozka,,hustota_bet
    MPDATA,DENS,podlozka,,0.98*hustota_bet
    MPDATA,DENS,podlozka,,0.95*hustota_bet
    MPDATA,DENS,podlozka,,0.88*hustota_bet
    MPTEMP,,,,,,,,
    MPTEMP,1,0
    MPTEMP,2,20
    MPTEMP,3,100
    MPTEMP,4,101
    MPTEMP,5,115
    MPTEMP,6,200
    MPTEMP,7,400
    MPTEMP,8,1200
    MPDATA,C,podlozka,,900
    MPDATA,C,podlozka,,1470
    MPDATA,C,podlozka,,1000
    MPDATA,C,podlozka,,1100
    MPTEMP,,,,,,,,
    MPTEMP,1,0
    MPTEMP,2,20
    MPTEMP,3,100
    MPTEMP,4,200
    MPTEMP,5,300
    MPTEMP,6,400
    MPTEMP,7,500
    MPTEMP,8,600
    MPTEMP,9,700
    MPTEMP,10,800
    MPTEMP,11,900
    MPTEMP,12,1000
    MPTEMP,13,1100
    MPTEMP,14,1200
    MPDATA,KXX,podlozka,,1.36
    MPDATA,KXX,podlozka,,1.333028
    MPDATA,KXX,podlozka,,1.2297
    MPDATA,KXX,podlozka,,1.1108
    MPDATA,KXX,podlozka,,1.0033
    MPDATA,KXX,podlozka,,0.9072
    MPDATA,KXX,podlozka,,0.8225
    MPDATA,KXX,podlozka,,0.7492
    MPDATA,KXX,podlozka,,0.6873
    MPDATA,KXX,podlozka,,0.6368
    MPDATA,KXX,podlozka,,0.5977
    MPDATA,KXX,podlozka,,0.57
    MPDATA,KXX,podlozka,,0.5537
    MPDATA,KXX,podlozka,,0.5488
    ! ------- MESHING --------
    KSEL,S,LOC,X,0,xxxx-yyyy
    LSLK,S,1
    ASLL,S,1
    VSLA,S,1
    VATT,beton,beton,beton,,beton
    KSEL,S,LOC,x,xxxx-yyyy,xxxx+yyyy
    LSLK,S,1
    ASLL,S,1
    VSLA,S,1
    VATT,podlozka,podlozka,podlozka,,podlozka
    ALLS
    VMESH,ALL
    /PNUM,MAT,1
    /NUMBER,1
    EPLO
    ! ------- DEFINOVANIE VYSTUZE -------
    ocel=632 ! OZNACENIE ELEMENTU <-----
    hustota_ocel =7850!
    poisson_ocel=0.3
    priemer=12! [mm]
    pi=acos(-1)
    plochavystuze=pi*(priemer/1000)*priemer/4000
    ET,ocel,REINF264
    priemer_horna=8! [mm]
    priemer_strm=6! [mm]
    plocha_hore=pi*(priemer_horna/1000)*priemer_horna/4000
    plocha_strm=pi*(priemer_strm/1000)*priemer_strm/4000
    v_hore = ocel+1
    v_strm_z= ocel+2
    v_strm_y= ocel+3
    SECT,ocel,REINF,DISCRETE,prut
    SECDATA,ocel,plochavystuze,EDGo,3, 0.5,0.5,0.5,0.5
    SECT,v_hore,REINF,DISCRETE,vyst_hore
    SECDATA,ocel,plocha_hore,EDGo,3, 0.5,0.5,0.5,0.5
    SECT,v_strm_z,REINF,DISCRETE,strm_z
    SECDATA,ocel,plocha_strm,EDGo,1, 0.5,0.5,0.5,0.5
    SECT,v_strm_y,REINF,DISCRETE,strm_y
    SECDATA,ocel,plocha_strm,EDGo,2, 0.5,0.5,0.5,0.5
    MPTEMP,,,,,,,,
    MPTEMP,1,0
    MPTEMP,2,20
    MPTEMP,3,100
    MPTEMP,4,200
    MPTEMP,5,300
    MPTEMP,6,400
    MPTEMP,7,500
    MPTEMP,8,600
    MPTEMP,9,700
    MPTEMP,10,800
    MPTEMP,11,900
    MPTEMP,12,1000
    MPTEMP,13,1100
    MPTEMP,14,1200
    MPDATA,EX,ocel,,200000E6
    MPDATA,EX,ocel,,180000E6
    MPDATA,EX,ocel,,160000E6
    MPDATA,EX,ocel,,140000E6
    MPDATA,EX,ocel,,120000E6
    MPDATA,EX,ocel,,62000E6
    MPDATA,EX,ocel,,26000E6
    MPDATA,EX,ocel,,18000E6
    MPDATA,EX,ocel,,14000E6
    MPDATA,EX,ocel,,8000E6
    MPDATA,EX,ocel,,4000E6
    MPDATA,EX,ocel,,1
    MPTEMP,,,,,,,,
    MPTEMP,1,0
    MPTEMP,2,1200
    MPDATA,NUXY,ocel,,poisson_ocel
    !  Multilinear isotropic hardening; valcované za tepla
    TB,MISO,ocel,14,14,0
    TBTEMP,0
    TBPT,,0,0
    TBPT,,0.00316,632E6
    TBPT,,0.15,632.01E6
    TBTEMP,20
    TBPT,,0,0E6
    TBPT,,0.00316,632E6
    TBPT,,0.15,632.01E6
    TBTEMP,100
    TBPT,,0,0E6
    TBPT,,0.00316,632E6
    TBPT,,0.15,632.01E6
    TBTEMP,200
    TBPT,,0,0E6
    TBPT,,0.002844,511.92E6
    TBPT,,0.0044,559.14E6
    TBPT,,0.0059,578.27E6
    TBPT,,0.0074,591.87E6
    TBPT,,0.0089,602.33E6
    TBPT,,0.0104,610.61E6
    TBPT,,0.0119,617.2E6
    TBPT,,0.0134,622.39E6
    TBPT,,0.0149,626.35E6
    TBPT,,0.0164,629.22E6
    TBPT,,0.0179,631.06E6
    TBPT,,0.02,632E6
    TBPT,,0.15,632.01E6
    TBTEMP,300
    TBPT,,0,0E6
    TBPT,,0.0024095,385.52E6
    TBPT,,0.004,475.12E6
    TBPT,,0.0055,515.21E6
    TBPT,,0.007,544.04E6
    TBPT,,0.0085,566.37E6
    TBPT,,0.01,584.15E6
    TBPT,,0.0115,598.39E6
    TBPT,,0.013,609.7E6
    TBPT,,0.0145,618.46E6
    TBPT,,0.016,624.92E6
    TBPT,,0.0175,629.26E6
    TBPT,,0.02,632E6
    TBPT,,0.15,632.01E6
    TBTEMP,400
    TBPT,,0,0E6
    TBPT,,0.001896,265.44E6
    TBPT,,0.0035,384.7E6
    TBPT,,0.0051,448.84E6
    TBPT,,0.0067,495.12E6
    TBPT,,0.0083,530.93E6
    TBPT,,0.0099,559.33E6
    TBPT,,0.0115,581.92E6
    TBPT,,0.0131,599.69E6
    TBPT,,0.0147,613.24E6
    TBPT,,0.0163,622.96E6
    TBPT,,0.0179,629.11E6
    TBPT,,0.02,632E6
    TBPT,,0.15,632.01E6
    TBTEMP,500
    TBPT,,0,0E6
    TBPT,,0.001896,227.52E6
    TBPT,,0.0035,317.39E6
    TBPT,,0.0051,363.28E6
    TBPT,,0.0067,396.17E6
    TBPT,,0.0083,421.54E6
    TBPT,,0.0099,441.63E6
    TBPT,,0.0115,457.6E6
    TBPT,,0.0131,470.15E6
    TBPT,,0.0147,479.72E6
    TBPT,,0.0163,486.58E6
    TBPT,,0.0179,490.92E6
    TBPT,,0.02,492.96E6
    TBPT,,0.15,492.97E6
    TBTEMP,600
    TBPT,,0,0E6
    TBPT,,0.00183483870967742,113.76E6
    TBPT,,0.0034,170.38E6
    TBPT,,0.005,202.95E6
    TBPT,,0.0066,226.56E6
    TBPT,,0.0082,244.87E6
    TBPT,,0.0098,259.42E6
    TBPT,,0.0114,271.02E6
    TBPT,,0.013,280.16E6
    TBPT,,0.0146,287.15E6
    TBPT,,0.0162,292.2E6
    TBPT,,0.0178,295.43E6
    TBPT,,0.02,297.04E6
    TBPT,,0.15,297.05E6
    TBTEMP,700
    TBPT,,0,0E6
    TBPT,,0.00170153846153846,44.24E6
    TBPT,,0.0033,72.96E6
    TBPT,,0.0049,90.95E6
    TBPT,,0.0065,104.34E6
    TBPT,,0.0081,114.84E6
    TBPT,,0.0097,123.25E6
    TBPT,,0.0113,129.99E6
    TBPT,,0.0129,135.33E6
    TBPT,,0.0145,139.43E6
    TBPT,,0.0161,142.41E6
    TBPT,,0.0177,144.34E6
    TBPT,,0.02,145.36E6
    TBPT,,0.15,145.37E6
    TBTEMP,800
    TBPT,,0,0E6
    TBPT,,0.00175555555555556,31.6E6
    TBPT,,0.0034,44.73E6
    TBPT,,0.005,51.17E6
    TBPT,,0.0066,55.8E6
    TBPT,,0.0082,59.37E6
    TBPT,,0.0098,62.21E6
    TBPT,,0.0114,64.46E6
    TBPT,,0.013,66.24E6
    TBPT,,0.0146,67.6E6
    TBPT,,0.0162,68.58E6
    TBPT,,0.0178,69.21E6
    TBPT,,0.02,69.52E6
    TBPT,,0.15,69.53E6
    TBTEMP,900
    TBPT,,0,0E6
    TBPT,,0.00180571428571429,25.28E6
    TBPT,,0.0034,30.08E6
    TBPT,,0.005,32.15E6
    TBPT,,0.0066,33.62E6
    TBPT,,0.0082,34.74E6
    TBPT,,0.0098,35.63E6
    TBPT,,0.0114,36.34E6
    TBPT,,0.013,36.9E6
    TBPT,,0.0146,37.32E6
    TBPT,,0.0162,37.63E6
    TBPT,,0.0178,37.82E6
    TBPT,,0.02,37.92E6
    TBPT,,0.15,37.93E6
    TBTEMP,1000
    TBPT,,0,0E6
    TBPT,,0.00158,12.64E6
    TBPT,,0.0032,17.17E6
    TBPT,,0.0048,19.28E6
    TBPT,,0.0064,20.79E6
    TBPT,,0.008,21.95E6
    TBPT,,0.0096,22.87E6
    TBPT,,0.0112,23.6E6
    TBPT,,0.0128,24.18E6
    TBPT,,0.0144,24.63E6
    TBPT,,0.016,24.95E6
    TBPT,,0.0176,25.16E6
    TBPT,,0.02,25.28E6
    TBPT,,0.15,25.29E6
    TBTEMP,1100
    TBPT,,0,0E6
    TBPT,,0.00158,6.32E6
    TBPT,,0.0032,8.59E6
    TBPT,,0.0048,9.64E6
    TBPT,,0.0064,10.39E6
    TBPT,,0.008,10.97E6
    TBPT,,0.0096,11.43E6
    TBPT,,0.0112,11.8E6
    TBPT,,0.0128,12.09E6
    TBPT,,0.0144,12.31E6
    TBPT,,0.016,12.48E6
    TBPT,,0.0176,12.58E6
    TBPT,,0.02,12.64E6
    TBPT,,0.15,12.65E6
    TBTEMP,1200
    TBPT,,0,0
    TBPT,,0.15,0.15
    ! Sucinitel dlzkovej teplotnej roztaznosti ocele
    ! Betonarska ocel
    MPTEMP,,,,,,,,
    MPTEMP,1,0
    MPTEMP,2,20
    MPTEMP,3,100
    MPTEMP,4,200
    MPTEMP,5,300
    MPTEMP,6,400
    MPTEMP,7,500
    MPTEMP,8,600
    MPTEMP,9,750
    MPTEMP,10,860
    MPTEMP,11,1000
    MPTEMP,12,1100
    MPTEMP,13,1200
    MPDATA,THSX,ocel,,0
    MPDATA,THSX,ocel,,0
    MPDATA,THSX,ocel,,0.0009984
    MPDATA,THSX,ocel,,0.0023184
    MPDATA,THSX,ocel,,0.0037184
    MPDATA,THSX,ocel,,0.0051984
    MPDATA,THSX,ocel,,0.0067584
    MPDATA,THSX,ocel,,0.0083984
    MPDATA,THSX,ocel,,0.011
    MPDATA,THSX,ocel,,0.0138
    MPDATA,THSX,ocel,,0.0158
    MPDATA,THSX,ocel,,0.0178
    ! hustota ocele
    MPTEMP,,,,,,,,
    MPTEMP,1,0
    MPTEMP,2,1200
    MPDATA,DENS,ocel,,hustota_ocel
    ! Definicia mernej tepelnej kapacity oceli c [J/ (kg*K) ]
    MPTEMP,,,,,,,,
    MPTEMP,1,0
    MPTEMP,2,20
    MPTEMP,3,100
    MPTEMP,4,200
    MPTEMP,5,300
    MPTEMP,6,400
    MPTEMP,7,500
    MPTEMP,8,600
    MPTEMP,9,690
    MPTEMP,10,700
    MPTEMP,11,710
    MPTEMP,12,720
    MPTEMP,13,730
    MPTEMP,14,735
    MPTEMP,15,740
    MPTEMP,16,750
    MPTEMP,17,760
    MPTEMP,18,770
    MPTEMP,19,780
    MPTEMP,20,790
    MPTEMP,21,800
    MPTEMP,22,900
    MPTEMP,23,1200
    MPDATA,C,ocel,,425
    MPDATA,C,ocel,,440
    MPDATA,C,ocel,,488
    MPDATA,C,ocel,,530
    MPDATA,C,ocel,,565
    MPDATA,C,ocel,,606
    MPDATA,C,ocel,,667
    MPDATA,C,ocel,,760
    MPDATA,C,ocel,,937
    MPDATA,C,ocel,,1008
    MPDATA,C,ocel,,1130
    MPDATA,C,ocel,,1388
    MPDATA,C,ocel,,2291
    MPDATA,C,ocel,,5000
    MPDATA,C,ocel,,2525
    MPDATA,C,ocel,,1483
    MPDATA,C,ocel,,1159
    MPDATA,C,ocel,,1002
    MPDATA,C,ocel,,909
    MPDATA,C,ocel,,847
    MPDATA,C,ocel,,803
    MPDATA,C,ocel,,650
    MPDATA,C,ocel,,650
    MPTEMP,,,,,,,,
    MPTEMP,1,0
    MPTEMP,2,800
    MPTEMP,3,1200
    MPDATA,KXX,ocel,,54
    MPDATA,KXX,ocel,,27.3
    ! ------- OKRAJOVE PODMIENKY -------
    NSEL,S,LOC,X,xxxx
    NSEL,R,LOC,Y,-1*yyyy
    D,ALL, , , , , ,UY,UZ
    NSEL,S,LOC,X,0
    D,ALL, , , , , ,UX
    NSEL,S,LOC,Z,0
    NSEL,A,LOC,Z,zzzz
    D,ALL, , , , , ,UZ
    ALLS
    ! EPLO
    edited July 2018
    hello Sandeep,
    those above are the setting for material models. After that, elements along the lenght of the "beam" - actually a piece of "slab" as some kind of plane stress is modelled are chosen and the reinf 264 is applied.
    the temperature load is here:
    edited July 2018
    tepl_refer = 20
    cas_horenia=240 ! minut
    ! ------- APLIKOVANIE ZATAZENIA -------
    ! ------- NASTAVENIE RIESICA -------
    /SOLU
    ANTYPE,4! transient analysis
    TRNOPT,FULL! full transient analysis
    KBC,0! ramp loads up and down
    ! Time stepping
    TIME,60*cas_horenia! end time for load step
    AUTOTS,ON! use automatic time stepping
    ! substep size (seconds) ! minimum value shorter than smallest time change in the table arrays below
    DELTIM,10,5,12.2
    OUTRES,ALL,ALL
    ! LNSRCH,1
    ! NEQIT,100
    ! LUMPM,0
    TREF,tepl_refer
    ! K?ivka normová : 20 + 345 log10 (8t + 1)
    *DIM,TEPLOTA,TABLE,37,1,1,TIME,,,0
    *SET,TEPLOTA(0,1,1),0
    *SET, TEPLOTA (1 , 0,1), 0
    *SET, TEPLOTA (2 , 0,1), 15
    *SET, TEPLOTA (3 , 0,1), 30
    *SET, TEPLOTA (4 , 0,1), 45
    *SET, TEPLOTA (5 , 0,1), 60
    *SET, TEPLOTA (6 , 0,1), 120
    *SET, TEPLOTA (7 , 0,1), 180
    *SET, TEPLOTA (8 , 0,1), 240
    *SET, TEPLOTA (9 , 0,1), 300
    *SET, TEPLOTA (10 , 0,1), 360
    *SET, TEPLOTA (11 , 0,1), 420
    *SET, TEPLOTA (12 , 0,1), 480
    *SET, TEPLOTA (13 , 0,1), 540
    *SET, TEPLOTA (14 , 0,1), 600
    *SET, TEPLOTA (15 , 0,1), 1200
    *SET, TEPLOTA (16 , 0,1), 1800
    *SET, TEPLOTA (17 , 0,1), 2400
    *SET, TEPLOTA (18 , 0,1), 3000
    *SET, TEPLOTA (19 , 0,1), 3600
    *SET, TEPLOTA (20 , 0,1), 4200
    *SET, TEPLOTA (21 , 0,1), 4800
    *SET, TEPLOTA (22 , 0,1), 5400
    *SET, TEPLOTA (23 , 0,1), 6000
    *SET, TEPLOTA (24 , 0,1), 6600
    *SET, TEPLOTA (25 , 0,1), 7200
    *SET, TEPLOTA (26 , 0,1), 7800
    *SET, TEPLOTA (27 , 0,1), 8400
    *SET, TEPLOTA (28 , 0,1), 9000
    *SET, TEPLOTA (29 , 0,1), 9600
    *SET, TEPLOTA (30 , 0,1), 10200
    *SET, TEPLOTA (31 , 0,1), 10800
    *SET, TEPLOTA (32 , 0,1), 11400
    *SET, TEPLOTA (33 , 0,1), 12000
    *SET, TEPLOTA (34 , 0,1), 12600
    *SET, TEPLOTA (35 , 0,1), 13200
    *SET, TEPLOTA (36 , 0,1), 13800
    *SET, TEPLOTA (37 , 0,1), 14400
    *SET, TEPLOTA (1 , 1,1), 20
    *SET, TEPLOTA (2 , 1,1), 185
    *SET, TEPLOTA (3 , 1,1), 261
    *SET, TEPLOTA (4 , 1,1), 312
    *SET, TEPLOTA (5 , 1,1), 349
    *SET, TEPLOTA (6 , 1,1), 445
    *SET, TEPLOTA (7 , 1,1), 502
    *SET, TEPLOTA (8 , 1,1), 544
    *SET, TEPLOTA (9 , 1,1), 576
    *SET, TEPLOTA (10 , 1,1), 603
    *SET, TEPLOTA (11 , 1,1), 626
    *SET, TEPLOTA (12 , 1,1), 645
    *SET, TEPLOTA (13 , 1,1), 663
    *SET, TEPLOTA (14 , 1,1), 678
    *SET, TEPLOTA (15 , 1,1), 781
    *SET, TEPLOTA (16 , 1,1), 842
    *SET, TEPLOTA (17 , 1,1), 885
    *SET, TEPLOTA (18 , 1,1), 918
    *SET, TEPLOTA (19 , 1,1), 945
    *SET, TEPLOTA (20 , 1,1), 968
    *SET, TEPLOTA (21 , 1,1), 988
    *SET, TEPLOTA (22 , 1,1), 1006
    *SET, TEPLOTA (23 , 1,1), 1022
    *SET, TEPLOTA (24 , 1,1), 1036
    *SET, TEPLOTA (25 , 1,1), 1049
    *SET, TEPLOTA (26 , 1,1), 1061
    *SET, TEPLOTA (27 , 1,1), 1072
    *SET, TEPLOTA (28 , 1,1), 1082
    *SET, TEPLOTA (29 , 1,1), 1092
    *SET, TEPLOTA (30 , 1,1), 1101
    *SET, TEPLOTA (31 , 1,1), 1110
    *SET, TEPLOTA (32 , 1,1), 1118
    *SET, TEPLOTA (33 , 1,1), 1126
    *SET, TEPLOTA (34 , 1,1), 1133
    *SET, TEPLOTA (35 , 1,1), 1140
    *SET, TEPLOTA (36 , 1,1), 1146
    *SET, TEPLOTA (37 , 1,1), 1153
    ! /title,TEPLOTA vs CAS normova krivka
    ! *VPLOT,TEPLOTA(1,0),TEPLOTA(1,1)
    ! /ui,copy,save,png,graph,color,reverse,portrait,yes
    ! /ui,copy,save,png,graph,mono,reverse,portrait,yes
    ! /title
    *DIM,ERKO,TABLE,2,1,1,TIME,,,0
    *SET,ERKO(0,1,1),0
    *SET, ERKO (1 , 0,1), 0
    *SET, ERKO (2 , 0,1), 14400
    *SET, ERKO (1 , 1,1), 1000
    *SET, ERKO (2 , 1,1), 1000
    NSEL,S,LOC,Y,-1*yyyy
    SF,ALL,CONV, %ERKO% , %TEPLOTA%
    ALLS
    *DIM,HORE,TABLE,2,1,1,TIME,,,0
    *SET,HORE(0,1,1),0
    *SET, HORE (1 , 0,1), 0
    *SET, HORE (2 , 0,1), 14400
    *SET, HORE (1 , 1,1), 20
    *SET, HORE (2 , 1,1), 20
    *DIM,ERKO_HORE,TABLE,2,1,1,TIME,,,0
    *SET,ERKO_HORE(0,1,1),0
    *SET, ERKO_HORE (1 , 0,1), 0
    *SET, ERKO_HORE (2 , 0,1), 14400
    *SET, ERKO_HORE (1 , 1,1), 1
    *SET, ERKO_HORE (2 , 1,1), 1
    !NSEL,S,LOC,Y,yyyy
    !SF,ALL,CONV, %ERKO_HORE% , %HORE%
    ALLS
    edited July 2018
    actually in this case it was not working as well - i mean with the "tref,20" - I needed to put tref,15 - but it does not really matter, as +/- 5°C is almost nothing there.
  • jpasquerelljpasquerell Canonsburg, PAMember
    edited July 2018
    Dadojin:
    Try adding an ERESX,NO command prior to the SOLVE. Often the extrapolation of linear results appears as though the stresses are off the stress strain curve.
  • jjdoylejjdoyle PittsburghMember
    edited July 2018
    Lots of temperature dependent materials.  What if you take out all temperature dependence (as a test)?
     aAlso SOLID226 is higher order, SOLID185 is lower order, ...and both element types have different KEYOPT switches.  You should refer to the elements manual docs for each of these element types and go thru each element specification carefully to discover possible differences.  What about SOLID186?
    Also how localized is the result in question?  Perhaps there is enough of a difference in the integration point locations and densities that is causing some interpolation/extrapolation issues.
    Also, compare the two solver outputs side by side to consider the all the solver specifications and convergence tolerances that might be different.
    John
    edited July 2018
    thanks for the advices.
    in one temperature only (the normal one = 20°C), solid226 with reinf264 is working as well as solid185 with reinf264.
    however when it comes to temperature loads:
    in case of solid185 I insert load step from previous thermal transient analysis by solid70 elements. That is working for 2 cases - R30 and R60 (30 and 60 minutes of fire) fire resistance according to European standard. The resistance of the structure is a bit higher then what are the caculations by hand according to mentioned standard. In ansys I put the thermal field from the results file as 1st load step, and then putting pressure loads in next steps till it does not convergate.
    However when it comes to R90, the solution falls at approx. time 0,9 (time 1 is the temperature of R90 for the structure) - not talking about R120,180,240 - the structure should be definitelly resisting also these much higher temperatures.
    there is only little difference if i first put load and then temperature, or if i put it in once in one load step, there is smth wrong with the temperature which occurs in the structure in that particular moment somewhere.
    So I tried to use solid226 as well and to put there the temperature load. also working only till some point, however this stresses in reinforcement are weird. When I remove HSD2 from MW material model of concrete, in case of solid226 the solution goes till some 9875 seconds (0second is the initiation of the fire and 240*60 is 240 minutes of fire). after that it was possible to restart the solution form that step, it reached the 240th minute, but the results were this way wrong (stress in reinf.)
    in normal temperature, if in case of solid 185 the enhanced strain is used, it was not working, so full integration is being used since then.
    so far i have not used solid 186 - could give it a try as well
    edited July 2018
    The TB,CONC nonlinear material model is only used by SOLID65 (legacy) so it is not used by SOLID226 elements.
    edited July 2018
    See Chapter 4 of the Mechanical APDL Element Reference for a table of Element Support for Material Models.
    edited July 2018
    sure, but I am using menetrey willam - mat model, which is supported by solid 185 and also 186 and also solid 226 - it is working very well in case of 20°C
    edited July 2018
    it is defined through concrete,,,MW or smth like that like above
    edited July 2018
    How did you conclude that SOLID226 supports Menetrey-Willam?
    According to the Elements Manual, I only see Extended Drucker Prager concrete option listed under the SOLID226 element chapter.
    edited July 2018
    well, the same way it is not mentioned in case of solid185, which is perfectly working with MW mat model (see here: https://ansyshelp.ansys.com/account/secured?returnurl=/Views/Secured/corp/v190/ans_elem/elem_matsupp.html )
    so I just tried it, first with temperature 20°C, and the results were almost identical as when I used elements solid185.
    edited July 2018
    Thanks for this feedback.
    There appears to be an inconsistency in our documentation.
    The Table “Material Model Elements Support” (Chapter 2 of Material Reference Manual) lists the following elements as supporting 'CONCR - Menetry-Willam';
    "PLANE182 (excluding plane stress), PLANE183 (excluding plane stress), SOLID185 (excluding layered structural solid), SOLID186 (excluding layered structural solid), SOLID187CPT212CPT213CPT215CPT216CPT217"
    However the Table “Elements Support for Material Models” (Chapter 4 of Material Reference Manual) does not list Menetry-Willam under SOLID18x and CPTx elements.  It should.
    We will try to fix this inconsistency in future release.
    Thanks again for the feedback.