May 5, 2023 at 4:33 pm
onlycfd
SubscriberHello Fluent Experts,
Hope you are all doing great.
Would very much appreciate your thoughts and guidance on a technical challenge which I have been facing for quite some time.
A brief writeup on what is being performed in the simulation.
We have two chillers on a roof top. Each chiller has got 3 independent V circuits. We modeled two chillers as there is an uneven loading on the V circuits of the chillers (Not modeling the tubes and water flow inside. Taking into account only the air side pressure losses across the V coils)
Axial fans are modeled with the blade topography. Frame motion is assigned to the fan rotating domain, as well as to the blades of the fans. There is a mesh interface between rotating domains and stationary atmosphere region.
So, we assigned the loss coefficients to the porous coils, rpm to the rotating fan domains.
Mesh Orthogonal Quality is at 0.2
Have assigned pressure inlet on the sides (equal to 0) and pressure outlet at the top (equal to 0), trying to replicate stationary air at the far regions. We have data only for the RPM of the fans.
What is physically expected is due to the suction created by the rotating fans, atmosphere is sucked over the coils of the V, and pushed out in the upward direction to the atmosphere.
But that is not what we are seeing in the results.
First the velocity plot and the pressure plot do not look realistic. We see a high-pressure region till the far end of the outlet, which in turn is impacting the velocity field.
Would appreciate your guidance and thoughts as to what we are missing in the simulation model, like any corrections to be made w.r.t to the boundary conditions setup, etc.
Thanks a lot for your kind guidance and help
-
May 8, 2023 at 5:44 pm
Federico Alzamora Previtali
SubscriberHello,
I would suggest making a couple of velocity vector plots to see how the air is flowing through the coils and fans. You could make these in the plane through mid fans, but also through a plane perpendicular to this (cutting mid-way through 3 fans). Finally, a vector plot normal to the axial direction of the fans to ensure that the frame motion is behaving as expected.
-
May 9, 2023 at 9:08 am
Rob
Ansys EmployeeI suspect I know the reason: been there, made the same mistake. What is the operating density that you’ve set, what is the air density definition and please post a velocity vector plot (in plane) same surface as the others.
Nice to see someone modelling the baby fans, if fed properly they can grow... https://www.lngindustry.com/magazine/lng-industry/march-2011/
-
May 10, 2023 at 5:55 am
-
May 10, 2023 at 10:10 am
Rob
Ansys EmployeeOK, it's the operating density that's causing the problem. Look in https://ansyshelp.ansys.com/account/Secured?returnurl=/Views/Secured/corp/v231/en/flu_ug/flu_ug_bcs_sec_operating.html Section 7.3.1.5
Assuming you're not using high speed fans (ie over about 0.3M) use incompressible ideal gas as you don't need to worry about pressure effects: read up on why! If you look at the equation why do you think the flow is a bit odd?
-
- You must be logged in to reply to this topic.

Boost Ansys Fluent Simulations with AWS
Computational Fluid Dynamics (CFD) helps engineers design products in which the flow of fluid components is a significant challenge. These different use cases often require large complex models to solve on a traditional workstation. Click here to join this event to learn how to leverage Ansys Fluids on the cloud, thanks to Ansys Gateway powered by AWS.

Earth Rescue – An Ansys Online Series
The climate crisis is here. But so is the human ingenuity to fight it. Earth Rescue reveals what visionary companies are doing today to engineer radical new ideas in the fight against climate change. Click here to watch the first episode.

Ansys Blog
Subscribe to the Ansys Blog to get great new content about the power of simulation delivered right to your email on a weekly basis. With content from Ansys experts, partners and customers you will learn about product development advances, thought leadership and trends and tips to better use Ansys tools. Sign up here.
- Suppress Fluent to open with GUI while performing in journal file
- Floating point exception in Fluent
- What are the differences between CFX and Fluent?
- Heat transfer coefficient
- Getting graph and tabular data from result in workbench mechanical
- Difference between K-epsilon and K-omega Turbulence Model
- The solver failed with a non-zero exit code of : 2
- Time Step Size and Courant Number
- Mesh Interfaces in ANSYS FLUENT
- error: Received signal SIGSEGV
-
5454
-
3409
-
2473
-
1310
-
1022
© 2023 Copyright ANSYS, Inc. All rights reserved.